“We have an ISMA MIX-IP controller connected to a JACE 8000. Where should the control logic be programmed: in the ISMA controller or in the JACE?”

I’d put the logic in the JACE. One place to build it, trend it, and troubleshoot it. Benefit of the JACE is that you can easily query or cross-link live from other controllers without having to shutdown the equipment.

Ideally the MIX-IP has some basic logic to cover a JACE failure but likely the JACE failing is going to shutdown the majority of the site anyways. If this is a critical application you’d have to have a full backup program running in the MIX.

Loops can’t be tuned pretty easily by just slowing them down which is normal for most equipment.

What’s the MIX-IP running, a single AHU or a few pieces of equipment?

Thank you for your reply and for your time.

The iSMA-MIX-IP controllers are connected to the hot water system, which includes boilers, heat pumps, and transfer pumps.

Is the iSMA programming similar to the wire sheet logic used in Niagara JACE, or does it require a different programming approach?

I would appreciate your guidance on this.