Has anyone experienced communication or performance issues with Daikin ITM, Samsung, or LG Smart 5 systems when integrating them with a JACE?
We’ve been running into similar issues with all three manufacturers, and it seems like the devices may not be able to handle the amount of traffic generated by the JACE.
Daikin:
The ITM would eventually freeze under the communication load. We had to change points to read-only and adjust the tuning policies to reduce the traffic. The Daikin vendor ultimately recommended keeping the points read-only after the other adjustments we tried did not resolve the issue.
Samsung:
We’ve experienced similar behavior. Samsung provided a list of recommended tuning policy settings, but we are still having to keep the points read-only.
LG Smart 5:
This one is behaving a little differently. It appears to be writing True/False to Boolean points at what seems to be a fixed interval. For example, an Occupancy command point that is set to “Occupied” will periodically tell the LG Smart 5 that it is “Unoccupied.” It stays unoccupied for roughly 10 minutes before going back to occupied. We’re seeing similar behavior with the other Boolean points as well.
So far, we’ve tried:
-
Changing tuning policies from polling to COV
-
Adjusting tuning policy timing to reduce the frequency of communication with the JACE
-
Reducing the amount of traffic where possible
-
Setting points to read-only
The only solution that has consistently worked so far is keeping the points read-only.
We’re currently waiting for LG tech support to get back to us, but I wanted to see if anyone here has run into similar issues with these systems.
Has anyone found a solution that allows write commands from the JACE without overwhelming or causing issues with the equipment/controller? Any suggestions for tuning policies, communication settings, or other things we may be overlooking would be greatly appreciated.