[Challenge] - LUX Lighting Control

Objective:

Your task is to design an automatic lighting control system using primitive logic blocks in Niagara 4 (N4). The system should control lighting based on occupancy and ambient light levels, ensuring energy efficiency and user comfort.

:woman_technologist: This challenge is intended to test your ability to interpret functional specifications and implement them using Niagara’s primitive logic blocks. It’s a simulation of how you might translate a consultant’s specifications into a working control strategy.


Instructions:

Setup:

  • Inputs:
    • OccupancySensor (boolean): Indicates room occupancy (true for occupied, false for unoccupied).
    • AmbientLightLevel (numeric): Measures the current light level in lux.
    • TimeSchedule (boolean): Active during building operating hours.
  • Parameters:
    • LightLevelSetpoint (numeric): Desired ambient light level in lux (e.g., 500 lux).
    • OccupancyTimeout (numeric): Time in minutes before lights turn off after the room becomes unoccupied (e.g., 15 minutes).
  • Outputs:
    • LightingControl (boolean): Controls the lighting (true for on, false for off).

Logic Requirements:

Basic Operation:

  1. Occupied Mode:
  • When OccupancySensor is true and TimeSchedule is active:
    • If AmbientLightLevel is below the LightLevelSetpoint, set LightingControl to true.
    • If AmbientLightLevel is equal to or above the LightLevelSetpoint, set LightingControl to false.
  1. Unoccupied Mode:
  • When OccupancySensor changes from true to false:
    • Start a timer for OccupancyTimeout minutes.
    • After the timer elapses, set LightingControl to false regardless of AmbientLightLevel.

Manual Override:

  • Implement a ManualOverride (boolean) input that, when true, forces LightingControl to remain true regardless of other conditions.
  • The manual override should be reset automatically at the start of the next TimeSchedule active period.

Safety and Energy Efficiency:

  • Ensure that lights do not flicker or toggle rapidly due to fluctuations in AmbientLightLevel or sensor noise.
  • Implement a deadband or hysteresis around the LightLevelSetpoint to prevent unnecessary switching.

Tools:

  • Use primitive logic blocks such as Comparators, Timers, Latches, And, Or, Not, and Hysteresis blocks available in Niagara 4.
  • Design the logic to handle all specified modes and conditions, ensuring smooth transitions and stable operation.

Testing:

  1. Simulate Occupancy:
  • Change OccupancySensor between true and false states.
  • Verify that LightingControl responds correctly, including the OccupancyTimeout delay.
  1. Adjust Ambient Light Levels:
  • Vary the AmbientLightLevel input to test the system’s response to changing light conditions.
  • Confirm that the deadband or hysteresis prevents rapid toggling.
  1. Test Time Schedule:
  • Simulate the TimeSchedule being active and inactive.
  • Ensure that lights turn off when the schedule is inactive, regardless of occupancy.
  1. Manual Override:
  • Activate ManualOverride and verify that LightingControl remains true.
  • Confirm that the manual override resets at the next scheduled period.

Submission:

  • File: Save and submit your completed Niagara 4 file (.bog) as a reply to this post.
  • Documentation: Include a brief explanation detailing how your logic works.

:no_entry: As always, the implementation may differ in the real world.

Good luck, and happy engineering! :rocket:

Excuse the newbie questions, but I’m trying be exhaustive in staying true to the SSO.

In the Basic Operations For Occupied mode it indicates “When OccupancySensor is true AND TimeSchedule is active”. Can I assume this means “OR” instead of “AND” as it seems likely that the intent is to have lighting active when either OccupancySensor senses people or the TimeSchedule is in the normal business hours? Or is there something I’m missing?

The intent is that the lights are occupied by the motion sensor but only during trading hours. The occupancy schedule governs this.

Understood. I was thinking lights on all the time during business hours with sensor override during afterhours. This is much better to save energy. This makes better sense. Thank you.

This is my submission for the Lux Lighting Control Challenge. It has 3 parts:

  1. Override Logic
  2. Occupancy Logic
  3. Light Level Logic

The Override logic uses a One-Shot Override Button in conjunction with the Boolean Schedule to reset that logic when the Next time Schedule turns to active (Uses a One-Shot from the schedule to combine with Override One-Shot to trigger a Boolean Switch) The state of the switch is fed by the True state of whichever Trigger is used.

The occupancy logic uses uses a direct connection to the output in combination with aNumeric Delay, fed from the Occupancy Timeout input, which is then fed to the Boolean Delay Block, which keeps the lights on for a configural delay time.

The Light Level Logic Uses a Deadband which is added and subtract from the Light Level Setpoint. This is fed through a Boolean Latch to basically the final output that is combined with the Override and Occupancy Logic to determine the state of the Boolean Writable Lighting Control Output.

These Challenges are so helpful for me to learn. I’m getting addicted!

LUX_Lighting_Control_Lee1.bog (2.4 KB)

@ControlFreak I’ll hopefully get to reviewing this, this week :smiley: I have not forgotten about you!

I think I get a better education with your challenges than doing a five-day cert class. And I see how much you guys do just on this platform (can’t imagine this is all on top of your daily jobs), so just whenever you get the chance. Absolutely loving this!!!

I’m learning when I see a lull in activity on DDC-talk, you guys are wicked busy! I’m spending my time doing deeper learning of N4, but when someone gets a chance to try to break my logic, would be curious if I stayed on the rails with this on. No time rush, just when its easiest! Cheers to all the moderators on this site.

Hi mate, still on my list :slight_smile:. We are in the middle of a heat wave and the Christmas rush! So you’re spot on, haha! Hopefully, someone else has a spare moment. Otherwise, usually between Christmas and New Year’s, there isn’t much going on, and I’ll take a look then :partying_face:.

Sorry its taken a while for this one, busiest time of year for us in Australia.

I’ll download this and test it out

It was a good effort. The only thing that really didn’t work was the override. The override was meant to work for any condition, regardless what was going on.


This is more just of a nitpicky thing, but I don’t think the numeric delay is needed. It can just be set to for a time and no need to delay that I don’t think, unless I read the instructions incorrectly.

However, I did find the issue with the override:

You’ll see my comment in the picture but perhaps you were trying to link the output of the schedule rather than the input. You can read what that’s for in the screenshot.

Lastly,

Clocks in the latch blocks are garbage, they don’t work really in the way you would truly want. Just link directly to the latch action to get the desired result. Add a delay in there for cornercase scenarios. I added comments in the picture :slight_smile:

Thanks for looking at this sir! I’ll have to look into that override logic to see where I went off into the weeds! Yeah, with the delay logic, I was trying to accomplish the criteria:

  • Parameters:
    • LightLevelSetpoint (numeric): Desired ambient light level in lux (e.g., 500 lux).
    • OccupancyTimeout (numeric): Time in minutes before lights turn off after the room becomes unoccupied (e.g., 15 minutes).

When I get a chance, I’ll go back in to see what I can do to make that override logic work better.
This is pure gold for me to have you guys critiquing my stuff so that I can modify and learn! Thank you again!

Realistically when you see the Occupancy timeout, I think of just a delay and only a delay. Nothing fancy, unless that was Giants goal.

You’re doing a great job by the way.

That is high praise coming from you, sir. I look in on the other categories that you guys are involved in to see what seem to be limitless possibilities with N4, and it sets my sights high. That you reach back down the ladder is…treasured!

Lights require 3 things to turn on: Schedule active, Occupancy active, and Light level to be less than the setpoint. Override is controlled by the Xor: When given a true, it holds the true until another true is given. Can be reset by refiring override or the schedule goes active while the override is active.


LUX.bog (2.7 KB)