Clear unacknowledged alarms - Program Object

Description
A tiny program object, that goes through all alarm extensions in the ord defined and resets all transition bits.

Once in a while, especially during engineering, if alarm extensions are enabled, you can end up with points that appear to be in alarm, even though they are not in the console or have been acknowledged. This is due to an error in the transition bits that sometimes occur in Niagara.

How to use

  1. Doubleclick on the program object and set the Ord. The program will search through all alarm extensions from this ord and down through all it’s subfolders.
  2. Right click the program object and select “Action”->“Execute”.

The program object is within this bog. Drag it into your N4 station
ClearUnack.bog (3.6 KB)

:warning: :warning:Station needs to restart after running the program!!! :warning: :warning:

3 Likes

Me likely, I’m going to add this one to the collection :sunglasses: